Hi All,

My question is basically about how much can you decrease the baseline capacities without going to far - that might call Red flags.

For example I have a baseline model that has 3 packaged VAV each having a total cooling capacity of about 650,000 Btuhs. My unmet hours on this project is around 96 hours. But I need to increase these unmet hours to meet the ASHRAE G3.1.2.2 requirement. I am asking because I only begin to see any increase in unmet hours when I drop the capacities to about 450,000 Btuh -  which to me seems like a lot. 

Any thoughts?

ASHRAE G3.1.2.2

“If unmet load hours in the proposed design exceed the unmet hour load hours in the baseline buildings by more than 50, simulated capacities in the baseline building shall be decreased incrementally and the building resimulated until the unmet load hours are within 50”