I have York Chillers which are used very rarely and only under extreme hot weather conditions, requiring additional cooling.

Unfortunately these Chillers still use R-11 CFC Refrigerant. They also fall under the criteria of Conversion would not make it Economically Feasable to convert. Including all the supporting documentation for annual controlling leak rate of 5% or less.

Does this mean we get kicked to the curb on this one and thers no way we can qualify. Or is it automatically excepted considering it meets E.A. Preq.3 requirement guidelines for CFC based refrigerants.
Please advise - Rey