FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

DCV modeling

Greetings, The project I'm modeling has several DOA AHUs. Every AHU has a single CO2 sensor located on the return duct next to the unit. There are however AHUs which are serving several different rooms, but the CO2 sensor is only one on the assembly part of the return duct. Should such units be modeled as DCV. There is another question to this issue. The number of people in the room (occupancy) is defined by the designers and these numbers do not coincide with min ASHRAE 62.1 rates (they are smaller). The OA air flows however, for both Proposed and Baseline are equal. Also the air quantity (cfm/pers & cfm/ft2) is as per ASHRAE 62.1 rates, only the Occupancy Density - not. The question is (in respond to the reviewers remark): How to make Baseline to reflect ASHRAE 62.1 min. rates whereas the OA is already defined by the Proposed and the occupant density do not coincide with ASHRAE 62.1 default values. Your advice on the matter will be highly appreciated. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/04/2014 - 17:00

In the system that serves multiple spaces with a CO2 sensor in one of the returns, you should only model DCV in the space served by the sensor and not in the other spaces. Do not use the ASHRAE default occupancy if you know the actual occupancy. The proposed outside air should be based on the design for all systems, in all cases. The Baseline outside air should be based on the ASHRAE 62,1-2007 calculated outside air from the corresponding system in the proposed if the proposed system has DCV. If it does not have DCV then the baseline is identical to the proposed.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.