NC-2009 IEQp1:Minimum indoor air quality performance

DCV control

Can someone help me with exception "b" of mandatory section 6.4.3.9 in 90.1. What is meant by the following: b. multiple zone systems without DDC of individual zones communicating with a central control panel. Must my client install DCV in an auditorium that meets all of the requirements of section 6.4.3.9 if the auditorium is fed by a multizone VAV system with DDC control? What damper would the DCV control?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 09/06/2013 - 16:30

If you have a normal VAV system with DDC control, exception b does not apply. Exception b could apply if you had a multi-zone system where each space with a thermostat had its own stand-alone control to modulate its damper, but did not have a VAV box controller communicating with a central DDC system. Yes, unless any of the other exceptions apply (a, c, or d), DCV is required in an auditorium fed by a multizone DDC VAV system that fits the parameters of 6.4.3.9. of ASHRAE 90.1-2007. A controls contractor I worked with recently said it normally works best to let the VAV box be controlled by temperature and use the DCV carbon dioxide sensor to control the outdoor air damper at the air handling unit. It can get tricky to satisfy both 90.1 and 62.1 while maintaining comfort conditions in the whole system, so the HVAC engineer should definitely look at the control sequence carefully. Depending on the envelope loads, etc. , it's possible the VAV zone damper for the auditorium would need to be forced open above minimum in some cases if the temperature is satisfied but the CO2 sensor is reading high. Hopefully there is plenty of heating capacity in the AHU and also reheat at the VAV box.

Fri, 09/06/2013 - 17:15

Kinda wierd to make an exception for a system that has stand alone controls for each zone that don't comunicate with the central control panel. I.e. Just because you dont have one installed doesnt mean that you cant have savings if you do install a VAV box with a communicating controller. The exception seems to be saying that since its too expensive to install a communicating controller then you dont need to install it.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.