FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

DCV In Baseline

Hi all, Modelling DCV has been discussed many times in this forum. I gone through and understand quite a bit. I am listing my understanding along with some quires. Any response is much appreciated. Our project is in Zone1A and is a metro transport building. project design considers Co2 sensors for DCV in zone level and system level in densely occupied area to meet the requirement of ASHRAE and LEED IEQC1 i.e. where the density is more than 25 people per 1000 sqft. Project also employs DOAS with Heat recovery to supply fresh air all the equipment inside the building i.e. AHU, FCU, CRAC. I modelled same outdoor air quantity for base and proposed case. My confusion is listed below and appreciate any clarification on this: 1. As some of the space meets the section 6.4.3.9, do I need to model DCV in Baseline? 2. I hope, the answer would be “yes” for my first question. In such case, how to model it in baseline. Let’s say there are 100 zones in a floor and 3 zones in that floor are highly occupied area (DCV required). There will be one system for the whole floor as per G3.1.1, which says, for systems 5,6,7and 8, each floor shall be modelled with a separate HVAC system. We can model DCV schedule in system level which will apply to all the zones served by the system. In this case, apart from these three zones, other 97 zones will have considered to have demand control ventilation. How to address this issue? FYI, I am using Equest software. 3. To address the above issue, can I provided separate system (System 3 or 4) for these zones only to model DCV as the Minimum OA schedule varies significantly w.r.t other zones served by this same system in baseline? 4. If the answer is no for my first question can I just model DCV in Proposed case and take credit? (hopefully the answer will be no). 5. The zones with high dense occupancy required to have DCV in base line has DCV control designed in the proposed case. Since DCV is required to be there in both base and proposed can I not model DCV in both the cases? Request prompt response and appreciate any response. Regards VEL

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 06/02/2017 - 13:08

1. Yes 2. I think you can enable DCV at the system level and then enter a specific constant cfm at the zone level for those zones without DCV and a cfm/person for zones with DCV. This would then map to the occupancy schedule for that space. 3. If you can't do the above then you should create a separate system with the same parameters (efficiency, etc.) as the system for that floor. You should explain what you have done in a narrative to the reviewer. 4. It is no. 5. You do model DCV in both cases and the quantity of outside air should be identical in these spaces.