some opertaive clarifications will be really appreciate: pursuing the credit through option 2
1. Do I have to select for the whole building the worst case form 9AM and 3PM, or do I have to select the worst case for each space (so that for some room I pick 9AM simulation results and for other the 3PM simulation results, that is what gives me romm-by-room the lower value of %A)?
2. Giving a literaly interpretation to record the areas that are daylit (have illuminance levels between 300 lux and 3,000 lux for both 9 A.M. and 3 P.M.) (reference guide, step-by-step guidance, option 2, step 3, 1st bullet point), should I take the green area form the schematic linked image, that is the intersection between grid points that have illuminance levels in 300-3000 lux thresholds at 9AM and grid points that have illuminance levels in 300-3000 lux thresholds at 3PM, that is room area daylit both on at 9AM and 3PM? This a more severe interpretation but may underline the concept that a desk station is not moving during the day; moreover it seems to me the literaly meaning of areas daylit bith 9AM and 3PM.
Thanks in advance
Alessandro
- The simulation is done for all regularly occupied space. The simulation must be carried out both in 9AM and 3PM for each regularly occupied space. You have to perform one illuminance simulation at 9 A.M. on the equinox (September 21 or March 21) and at 3 P.M. on the equinox (September 21 or March 21) for the second illuminance simulation.
- Yes, the daylighted regularly occupied area is the area that have both daylight in 9AM and 3PM.