Daylight Option 2 Grid Size

The LEED Reference Guide does not specify a grid size for daylight illuminance simulations.

I have been using the default 0.5 m grid spacing while simulating daylight illuminance using the software IESVE, but the simulations are taking a very long time, more than a day per floor.

What is the maximum allowable grid spacing for Option 2?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 04/08/2024 - 02:18

Is this question solved? Information for other users, the grid size for daylight simulation is defined in the IES LM 83-12. It is two feet maximum. I wish it might help Ziad and others.