CS-2009 PIf3:Occupant and Usage Data

C&S Default Occupancy counts for Assembly usage

Hi, We have a CS v2009 building that is a mixed use occupancy. We are trying to project the occupancy, A-3 General Assembly portion, using the default occupancy counts. Since Assembly is not listed in the CS Appendix 1 Default Occupancy Numbers where can we find the Number to use for employees and transients for the Assembly category to project the count? Thank you-

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 07/18/2016 - 20:07

Hi Cathy, In ASHRAE 90.1-2007 User's Manual, there is the Table G-B—Acceptable Occupant Densities, Receptacle Power Densities, and Service Hot Water Consumption. For the building type "Assembly", they suggest 50 ft2/person. I hope this helps.