Hello,

I´m modeling the garage fans in Proposed building in the following manner: double speed drive (1st step:50% airflow; 2nd step: 100%) with CO sensors located arround the park. When CO levels are below 50ppm, parking fans are at the lowest speed, but when those levels reach 100ppm, parking fans operate ate full speed.

As per ASHRAE 90.1 - 2010, section 6.4.3.4.5, garage fans do not need to stage/modulate if the one of the exceptions are met (the building falls under exception a, as the garage has arround 800m2 and does not have mechanical cooling or heating).

Since garage fans in 90.1 - 2010 are not considered a process load (as they are regulated), there is not the need to have equal energy consumption in both baseline and proposed.

My question is, may I take credit here by modeling the Baseline's garage fans as constant speed (as they are excepted to stage/modulate)?