Forum discussion

CI-2009 EAc1.3:Optimize energy performance - HVAC

Core Performance Compliance New Air-handler- Existing Chiller

If we specify a new air handler that uses steam and chilled water from existing systems, do these systems need to comply with the CPG efficiency requirements? We are looking to use Option 1. The air handler is a 5 HP VAV unit so it would just need a variable frequency drive, correct? Thank you,

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 11/27/2013 - 20:47

I don't think the existing systems would need to comply with the equipment efficiency requirements (2.9). The 5 HP VAV has to meet the criteria in 3.10. It is not just having a VFD. It requires that the control will result in fan motor demand of no more than 30% of design wattage at 50% of design flow.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.