FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Cooling plant modeling

In the project we are modeling the cooling plant which serves the production area and the buildings' HVAC systems is one and the same. Probably the designers' solution is such because the cold water temperature parameters are identical for the whole building. The chillers are with refrigerant ammonia. The following questions are open at the moment and we'd highly appreciate some assistance for their resolution. 1. Does the 90.1-2007 standard regulate ammonia refrigerant water cooled chillers? 2. The cooling circuit between chillers and the served cooling coils includes intermediate heat exchanger whereas the circuit between chillers and the heat exchanger are water/glycol mixture. The evaporator's outlet temperature is -2 oC (28.4 oF). Are chillers operating with these parameters considered as regulated by the standard and if not what parameters for the Baseline chillers are to be applied? The project belongs to System 7. 2. Having in mind that the production (and all of the systems assigned to it) are to be considered as process load and are to be identical to Proposed and Baseline models, should the cooling plant be split into two sections - one for the buildings' HVAC systems and the other for the production needs. 3. Assume we split the cooling plant. Regarding the chiller part assigned to the production, the question is: In case there is a better efficiency chiller than the project one and it is readily available on the market, could we apply an exceptional calculation for evaluating the savings resulted from the better efficiency chiller? Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 04/28/2016 - 15:07

1. Hard to say for sure. It depends on what type of chiller they are. Are these low temperature chillers? If so see the note under table 6.8.1C and Section 6.4.1.2. 2. See 6.4.1.2. 2. Yes you will need to separate the energy use of the chillers into space conditioning and process loads. 3. Yes. You do an exceptional calculation when claiming process load savings.

Thu, 04/28/2016 - 15:55

Hi Marcus, Thanks for the reply. It appears that these chillers are not covered by the standard as per 6.4.1.2. - they are low temperature, not very low but enough. The question then is: How to model the Baseline cooling plant in terms of chillers - should the chillers and the chillers' circuits be identical to Proposed?Baseline HVAC system will be System 7. Thanks

Thu, 04/28/2016 - 16:23

The Baseline chillers are still according to Table G3.1.3.7. Where you run into a potential issue is with the process load. That aspect of the models must be modeled identically. If the chillers are more efficient than the baseline you will need to do an exceptional calculation.

Fri, 04/29/2016 - 05:04

Thnaks a lot for the reply. I assume that the same approach should be applied to the heating plant - meaning to split the load between Manufascturing and HVAC systems. Thanks

Fri, 04/29/2016 - 14:18

Yep, same thing.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.