We received an comment review about a system 6 (PVAV w/ PFP boxes) baseline model in eQuest: The SV-A reports indicates that the cooling efficiencies for the HVAC systems were not correctly reflected in the Baseline model and the supply fan energy has not been broken out as required (per G 3.1.2.1). We responded with a revised EIR (not eQuest Default calculation) and a narrative explaining the deduction steps. But it again was denied by the reviewer.
My question is, in the appealing, am I supposed to keep fixating on the EIR calculation, or is there any other evidence of fan power being broken out in the SV-A report that I neglected before? Many thanks
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
June 4, 2013 - 10:06 am
The EIR value is the only thing in the SV-A report that addresses the break out of fan power. Perhaps the issue is not using the eQUEST default calculation. So keep fixating.