Convenience printers/copiers

How do we show that the printers/copiers to be installed are just convenience ones and therefore will not require separate exhaust?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/23/2023 - 09:23

Hello Mike, Were you able to get the information? I ask the same question. I'll appreciate your return, 

Wed, 08/23/2023 - 10:15

The answer is the printer capacity - there's a maximum capacity (which I do not remember unfortunately) for convenience printers.  I expect you'll have to read the reference guide in detail to find this info. 

Wed, 08/23/2023 - 15:31

Hi Sara - Printers/copiers used to produce less than 40,000 pages/month are considered convenience printers/copiers for the purpose of this credit. Anything over this figure is considered to be 'high volume'. There are few related interpretations, but here is one if you need for reference: https://www.usgbc.org/leedaddenda/1938