FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Continuous insulation - Interrupted by slab vs truly continuous

Hi, I am modeling a masonry building. There have been discussions about whether the insulation should go on the outside (therefore truly continuous) with an extra veneer to finish or on the inside (interrupted only by the slabs on each floor). It does not look like ASHRAE 90.1 deals with this situation very well (e.g gives much guidance). Using Appendix A, Table A3.1A gives U Values for masonry walls with continuous insulation Uninterrupted by Framing. Neither of the cases are interrupted by framing however is it fair to use the same table in both scenarios for the energy model? Thanks Victoria

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 09/04/2014 - 07:48

I think that the insulation is better on the outside side for three reasons: 1. the thermal bridges are reduced 2. condensation problems inside the wall are less probable 3. you have more thermal inertia for the indoor space. I don't know exactly how ASHRAE is considering the issue. I'm looking forward to reading other comments. Regards

Fri, 09/05/2014 - 13:32

I agree with Francesco. Continuous insulation and thermal mass are the important considerations. As far as Appendix A make sure you read the assumed layers that are used to derive the values in the tables. So in this case read all of A3.1 since it describes the assumptions that went into the numbers in the tables. If your situation varies you need to make reasonable adjustments to derive your U-factor. In one scenario you have continuous insulation and the other you do not. So if the basis of the table is continuous insulation then you would need to make adjustments to the overall assembly U-factor.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.