FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Construction Details in Baseline Model

In ASHRAE90.1-2007, the construction type and U value of Baseline Model is regulated. We use EnergyPlus to do energy modeling, so there is a problem, where can we find standard construction detail for Baseline model to input information in EnergyPlus? or we just need to model as a typical construstion detial, and then adjust the U value of this typical construction the same as ASHRAE? does GBCI need a standard construction detail with correct U value? or just typical detail with correct U value? Thanks!

4

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/01/2011 - 07:20

You can refer to Appendix A of ASHRAE 90.1 for baseline constructions.

Mon, 09/19/2011 - 16:06

Appendix A is typically applied to the Proposed constructions. For the Baseline GBCI simply looks for the correct U-value, not a specific detail.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.