At first I thought we had this credit in the bag because we were maintaining somewhere around 70% of existing walls, floors, ceilings, etc. That is to say-what was in our space to begin with (that was non-structural and non-shell) was mostly being reused. After getting into the form on LEED Online, it seems to be a whole different story! Apparently I have to enter in not only what was existing and what was retained but also what the final square footage of new construction was. This seems to me completely arbitrary and in direct conflict of the credit intent and language. " Maintain at least 40% or 60% by area of the existing non-shell and non-structural components." I don't understand what any new construction on my project has to do with what we reused that was already existing. Does anyone have guidance as to if I am interpreting this correctly or not? Or any experience in documenting this credit?
Thank you
-leslie
David Posada
Integrated Design & LEED SpecialistSERA Architects
LEEDuser Expert
1976 thumbs up
November 10, 2010 - 8:05 pm
Leslie,
Page 225 of the CI reference guide might explain why this is happening, but the rationale is a bit confusing.
In the % reuse calculation, the "Total Retained Components Area (sf)" is the numerator. The denominator is *either* the "Prior Condition Area (sf)" OR the "Completed Design Area (SF)" depending on which is larger. (All areas are surface areas)
Say, in one scenario, you retain 900 sf of the existing 1000 sf of interior walls. You'd think your reuse would be 90%. But if you now build an additional 1000 sf of new interior walls, say for additional offices or conference rooms your reuse percentage goes down to 45%. That's not what I expected either.
The Ref. Guide states:
"By using the larger of the 2 values in the denominator, this equation puts projects that have minimized materials use in the completed design on a level playing field with projects that have optimized reuse of components from the prior condition."
Thus, projects that have optimized reuse of existing components only get credit for that if they *also* minimize materials in the completed design. The more materials are used in the completed design, the more your percentage of reuse will go down.
The credit requirements state: "Maintain at least 40% or 60% of the existing non-shell, non structural components (e.g., walls, flooring and ceiling systems. The minimum percentage interior component reuse for each point threshold is as follows: Interior Reuse: 40%, 1 point, 60%, 2 points."
I think many of us have interpreted "40% or 60% of existing" to mean we only look at the percent retained of the existing "Prior Condition Area," regardless of how much material surface area is in the final completed design. The requirements here don't say "have 40% or 60% of the Completed Design Area material area consist of Retained Components."
It's worth noting that in CI v2.0 Reference Guide the credit requirements and calculations for this credit are defined essentially the same as they are in CI 2009. And in NC 2.2, for credit 1.3 it says to "use existing interior non-structural elements in at least 50% of the completed building," which is what we're finding this credit to be pushing us toward. So there is a precedent for the credit working this way.
The credit intent is to "conserve resources, reduce waste and reduce environmental impacts of new buildings as they relate to materials manufacturing and transport." So maybe it's appropriate for a project that both reuses interior components AND adds little new material to score higher than a similar project that reuses the same amount of existing materials, but uses more total materials. But since I can't think of other credits where we earn points for using less material overall is than if we use more materials, it doesn't seem fair to hold back points for doing so only on those projects that are pursuing the building reuse credit.
Leslie Jones
Interior DesignerFOX Architects
57 thumbs up
November 17, 2010 - 1:53 pm
Thank you David. This really helps explain the intent and clarifies what I should be calculating. I like the fact that they are rewarding reduced use of additional materials, I just had no idea that's what this credit was about until I read through the calculations in detail.