FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Conditioned floor

Hello I'm working on a project that has conditioned areas on 6 floors, but in two of those floors has only 5% of all conditioned area , can I consider these floors conditioned as the another floors (that have 95% of conditioned area) to compose the baseline system?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/04/2012 - 16:10

For the most part a floor is a floor especially if it contains conditioned space. See floor area definition. The only exceptions I can think of might be a mechanical penthouse or mezzanine. The floor area in Table G3.1.1A is qualified with the word conditioned. The number of floors is not. See G3.1.1.

Tue, 12/04/2012 - 17:15

Hello Marcus! Thanks for the answer but I still have a doubt. We must count all the building's stories to discover the system baseline in table G3.1.1.A, or just count the building's conditioned stories. Thanks again

Tue, 12/04/2012 - 17:43

You must count all the floors in our opinion.

Fri, 12/07/2012 - 06:23

Hi Marcus/All, Just to clarify. In the clause G3.1.1 of Appendix G, it was mentioned that "the baseline building design shall be based on usage, number of floors, conditioned floor area and heating source as specified in Table G3.1.1A". We have a six storey warehouse project with only less than 10% of the floor area is conditioned (about 100,000 ft2). According to Table G3.1.1A, since our building is more than 5 storey, we have to use System 7 or 8 even though our conditioned area is less than 150000ft2. Am I correct? Appreciate your advice. Many thanks.

Fri, 12/07/2012 - 14:31

Yes there is an "or" in between the number of floors and the square footage. So if either condition is present then that is the system type. Again this is our opinion and interpretation and I could understand another opinion based on just the conditioned floors. We do not think the standard language supports that interpretation however these issue are often not completely clear in all cases.