I am working on a project under LEED NC 2009 where the com Rooms and server rooms are served by computer room units (CRAC) with dehumidification and reheat. i have done some research and it is not clear how to model them.
I accordance with LEED, do I have to model them as process or under 90.1 section G 3. 1 .1 exception b. since the dominant system is 5.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5921 thumbs up
October 2, 2013 - 3:20 pm
Exception b applies to these spaces. ASHRAE 90.1-2010 includes a baseline for these systems in Table 6.8.1K.