NC-v4 EQp1:Minimum indoor air quality performance

compliance for naturally ventilated spaces

Referring to the FAQs fan-assisted ventilation in naturally ventilated spaces can be considered as mechanical ventilation. Can ceiling fans qualify as mechanical ventilation or it has to be a ducted system for compliance with the prerequisite EQ

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/31/2017 - 17:37

If the fan is just recirculating air in the space it is not "mechanical ventilation".

Add new comment