FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Common corridors in residential building

Hi Marcus, My current project is a 40-story hotel building, which has 35 residential levels and 5 non-residential public-space levels. On the residential levels, the common corridors are conditioned. My queries are: 1.) Are the common corridors on the residential levels considered non-residential spaces? 2.) If the answer to 1.) is yes, the total non-residential floor area will be 80,000 square feet, and these non-residential spaces are on more than 5 floors. How shall the baseline HVAC system for the non-residential spaces be defined? Does the "System 8" come into play in this case? Thank you very much!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 07/19/2016 - 15:19

1. I consider them residential as access to the room is their sole purpose. 2. NA

Fri, 06/18/2021 - 16:24

For ASHRAE 90.1-2010 Appendix G: When modeling corridors, how is G3.1.1 exception a being applied when the common area is larger than 20,000 ft2? Use additional system type(s) for nonpredominant conditions (i.e., residential/ nonresidential or heating source) if those conditions apply to more than 20,000 ft2 of conditioned floor area. Also 9. Thermal Blocks -- Multifamily Residential Buildings Residential spaces shall be modeled using at least one thermal block per dwelling unit, except that those units facing the same orientations may be combined into one thermal block. Corner units and units with roof or floor loads shall only be combined with units shoring these features. In Table G3.1.1A Baseline HVAC systems types in the note, defines Residential spaces Residential building types include dormitory, hotel, motel, and multifamily. Residential space types include guest rooms, living quarters, private living space, and sleeping quarters. Other building and space types are considered nonresidential. Where attributes make a building eligible for more than one baseline system type, use the predominant condition to determine the system type for the entire building except as noted in Exception a to Section G3.1.1. If the common area spaces in the building are more than 20,000 ft2, the corridors should be modeled with a different system and not the residential building type system. Similar language is in ASHRAE 90.1-2004, 2007, 2013, 2016 and 2019.

Fri, 06/18/2021 - 19:03

It's not - if the only occupancy on those floors is residential then the group of floors is looked at together as a "residential building" without regard to some minority subset of the spaces. 

Mon, 06/21/2021 - 13:37

Where is a building defined by “individual floors”?  Exceptions in G3.1.1 are for the entire building, not individual floors. This is not in ASHRAE 90.1 or any other code. ASHRAE 90.1 defines both “Residential building types” as well as “Residential spaces”, they also define "Residential". Corridors are not listed in these definitions. For "multifamily residential buildings", the corridor is considered a commercial space, due to it being a path of egress for not just one dwelling unit, but all the units on the floor.  Within Section 9: Lighting, corridors have a lighting power density and lighting control requirements whereas dwelling units themselves are exempt from a lighting power density within ASHRAE 90.1 per section 9.1.1. Even the definition within ASHRAE 90.1 defining residential: spaces in buildings used primarily for living and sleeping. Residential spaces include, but are not limited to, dwelling units, hotel/motel guest rooms, dormitories, nursing homes, patient rooms in hospitals, lodging houses, fraternity/ sorority houses, hostels, prisons, and fire stations. A corridor's primary use is not for living and sleeping.  A corridor is a transitory space used for ingress and egress from primary space types.

Thu, 07/15/2021 - 17:17

GBCI has typically allowed for flexibility in classifying residential corridors as either residential (since the footnote to Table G3.1.1A classifies certain building types such as dormitory, hotel, motel and multifamily as residential) or nonresidential (since the corridors are not in the examples of residential space types in the definitions or the footnote to Table G3.1.1A). 

Tue, 06/14/2022 - 14:35

See the example that is described by PNNL. The corridor is considered as common space for the residential building. The examples are on page 41 (3.8).  https://www.pnnl.gov/main/publications/external/technical_reports/PNNL-26917.pdf 

Wed, 07/27/2022 - 00:17

     