Forum discussion

EBOM-2009 EAc3.2:Performance measurement - system-level metering

Commercial Building with Tenant spaces fully submetered

I am wondering if a commercial building, where over 90% of the building is submetered tenant space would qualify for this credit. There are separate submeters for the tenants plug load/lighting and the AC usage. Thanks

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 02/16/2012 - 22:16

Tzvi This sounds like it might work, as long as the aggregate of the sub-metered data covers 40% of the total annual energy consumption and 80% of the largest energy use category, based on the energy use breakdown. But you also need to take into account base-building energy consumption in your break-down. Let me know if you have any other questions on this - the energy end-use break-down seems to be a driving point to achieving this credit. Thanks, Hannah