NC-2009 IEQc8.1:Daylight and views - daylight

Combined approach

We have a project that is going to use a combined approach due to overhangs and the prescriptive calcs not providing enough SF. I have casually measured the spaces and we exceed 20fc. We have one large room that I can easily do a 10 ft grid on, but we also have 10 small offices that are probably narrower than 10ft. How is it recommended that I measure this space? Can I make a smaller grid, so we can include an adequate portion of these offices? Or do I just measure in the corners? (or a set distance off the corners?)

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/11/2015 - 12:56

The 2010 addenda states that at least 4 measuring points are required per space. I know its an overkill in 10x10 spaces but that is what is needed.