FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Combination of New Build and Existing

Hello, I am working on the major renovation of an existing office building and new construction of a new entrance/reception atrium. Both aspects are being assessed under the one LEED submission, as both share the same physical space (high level walkways from the office building are located in the atrium at high level). As such the ASHRAE 90.1-2007 model comprises both buildings. My question is whether the model needs to be rotated for the 0, 90, 180 & 270deg rotations. From the guidance provided above existing buildings do not need to be rotated. However as there is an element of new build here, how should we deal with it? The existing element is much greater than the new build in terms of floor area. We have worked off the basis that we must rotate the model to date, however can we justify not rotating, as the orientation of the new build is effectively dictated by the existing (follows the outline of the existing building). Thanks!

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 10/13/2016 - 14:23

No need to rotate for a small addition. Buildings with up to 50% new construction do not need to be rotated. See the Advanced Energy Modeling Guide for LEED.

Mon, 10/24/2016 - 09:48

Thanks for clarifying Marcus!