NC-2009 IEQc1:Outdoor air delivery monitoring

CO2 sensors in return ductwork?

The CO2 sensors for this science building are in the return ductwork, not 3-6' from the floor. I'm telling the team that this is clearly not in compliance, but the Honeywell rep insists otherwise. He writes: "Most schools do not have the capability to utilize return air. The location of the CO2 sensor at your building provides a better representative reading in all areas. This sensor location has been approved on all of our LEED installations to date." Any thoughts on this?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 08/29/2012 - 16:25

C02 Sensors in the return ductwork can be very informative to your system's operation when serving large non densely occupied spaces with a central return duct. However, it does not meet the requirements (of this credit) for CO2 sensors in each densely occupied space.

Wed, 02/27/2013 - 19:05

Maura, what did you end up submitting for this credit? Have you received your review back and did it pass with the sensors in the return air ducts? Thanks!

Fri, 09/27/2013 - 15:50

if you listen to the principles of LEED webinar it clearly states that it cannot be in the return duct work... needs to be 3'-6' above the finished floor. I'd advise the Honeywell representative to look at the LEED Online form :)