Forum discussion

NC-2009 IEQc1:Outdoor air delivery monitoring

CO2 sensor alarm when conditions vary 10%

The credit template requires the CO2 sensors to be programmed to generate an alarm when the conditions vary by 10% or more from the design value. Currently we are designing a facility AHU and VAV BOXES that requires 4 rooms to have CO2 sensors, but wouldnt this requirement only apply to constant volume systems since the ventilation of the rooms would depend on the CO2 sensors therefore it would most of the time not be at full occupancy and most of the time below the minimum outdoor air required? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/17/2012 - 13:09

According to the credit language the CO2 sensor only requires an alarm either from the building automation system to the building operator, or as a visual or audible alert to the building occupants. It does not have to be tied to the HVAC system.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.