CO2 measurements

Hallo, In our project there are AHUs providing a mix of outdoor and return air. Due to the machine room layout, it is very difficult to measure outdoor airflow (cfm). There is a formula to calculate outdoor air supply using: -outdoor air supply (cfm) -CO2 levels in supply duct (ppm) -CO2 levels in return duct (ppm) -Outdoor CO2 levels (ppm) Does anyone have experience having this prerequisite approved with this method?

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 10/26/2016 - 20:10

Hi Gustavo, I haven't seen that formula used before but there is another method to approximate the OA flow based on the temperature of outdoor, mixed, and return air temperatures when the supply flow from the AHU is known. See section 7.6.3.3 in ASHRAE 111-2008. The trick however is that the approximation is only considered to be accurate if there is a temperature difference between 25 - 50 degrees between the outdoor air and return air temperatures.

Thu, 10/27/2016 - 18:27

Thanks! I didn't know this method. Actually the formula is very similar to the one measuring CO2 levels. I read it in one of the I-BEAM text modules and it is only is accurate if there is a difference of more than 200 ppm in each air stream.