We are working on a project that includes spaces used to manufacture healthcare instrumentation in a clean room environment.  The client’s Engineering Standards as well as ISO 14644-1 Standard for Clean Rooms require these rooms to operate with a minimum 25 air changes per hour while meeting comfort cooling and dehumidification for the regularly occupied spaces.  According to ASHRAE 90.1(2010) – 2.1, “This standard provides minimum energy efficiency requirements for the design, construction, and a plan for operation and maintenance of new equipment or building systems specifically identified in the standard that are part of industrial or manufacturing processes.”  Based on the previous remark, we do not see this as a process or unregulated load.  The LEED v4 reference guide defines process energy as “power resources consumed in support of a manufacturing, industrial, or commercial process OTHER THAN CONDITIONING SPACES AND MAINTAING COMFORT AND AMENITIES FOR BUILDING OCCUPANTS OF A BUILDING.”  The baseline system for this area is System No. 5 (Packaged DX w/ hot water reheat) where the supply air flow rates are designed based on “the air flow required to comply with applicable codes or accreditation standards” (Appendix G – G3.1.2.9.1) aka 25 ACH.  The proposed system is a VAV recirculation unit with a decoupled DOAS unit.

It is important to note, the baseline system could have been our proposed design and would meet all code requirements.  Not being able to take savings from our energy efficient design doesn’t seem to make much sense.

The first LEED review stated the following: a clean room application (airflow sized based upon a discharge air to room air delta T much lower than 20 °F (per G3.1.2.9.1) basis for the rooms to maintain a certain level of cleanliness rather than maintain thermal comfort of the occupants). In which case it would be expected that such a system is not covered under ASHRAE 90.1 - 2010 and would be considered a process load like other manufacturing systems.  As process systems, the cleanroom systems and all setpoints must be modeled identically in the Proposed and Baseline Cases, unless the exceptional calculation method is used”

Second review stated the following: “25 ACH significantly exceeds the airflow rate for standard HVAC systems designed to meet the needs of human comfort. ASHRAE 90.1-2007 Section 2.3 states that “The provisions of this standard do not apply to” “c. equipment and portions of building systems that use energy primarily to provide for industrial, manufacturing, or commercial processes”. However, ASHRAE 90.1-2010 expand the scope and Section 2 Scope indicates that ASHRAE 90.1-2010 applies to “new equipment or building systems specifically identified in the standard that are part of industrial or manufacturing processes”. ASHRAE 90.1-2010 User’s Manual Chapter 2 Scope clarifies the “Scope of Standard” specifically addressed in the ASHRAE 90.1-2010: laboratories, kitchen ventilation, data centers, and elevator cabs. Future addenda will likely address other manufacturing and/or industrial processes. The HVAC systems serving manufacture spaces are not specifically identified in the standard, therefore, considered as nonregulated energy loads.  Nonregulated energy loads must be modeled identically within the Proposed and Baseline Case models unless savings for these items are justified using the exceptional calculation method”

If we would like to attempt to gain some savings from this “process/unregulated load”, we’d need to submit using an Exceptional Calculation Method in comparison with the standard practice for a similar facility.  How do we know what is considered “Standard Practice”?  Can anyone offer guidance to this approach?  

Per ASHRAE 90.1-2010, section G2.5, Exceptional Calculation Methods shall be “used when the simulation program does not model a design, material, or device of the proposed design”.  That is not the case for this project as the simulation program can model the proposed HVAC system.

Although we disagree that this should be considered a process load, we offered the suggestion to size the baseline and proposed systems based solely on occupancy and load.  The additional airflow would be considered a “process load” and modeled identically in the baseline and proposed scenario.  This was not acceptable either.

Any guidance is greatly appreciated!