Forum discussion

NC-v4 EAc2:Optimize energy performance

Clarification on Design Supply Air Temperature for Baseline model with both heating and cooling

Hello Everyone, 

I’m working on an energy model for LEED compliance using ASHRAE 90.1-2010 Appendix G. For a baseline system that provides both cooling and heating (e.g., VAV with reheat), what should be the design supply air temperature to the zone?

Appendix G mentions:

  • For single-zone systems: supply air temperature is 20°F difference from the design room temperature.
  • For multi-zone systems: fixed values of 55°F for cooling and 95°F for heating.

My question:

  • If the baseline system is multi-zone VAV with reheat, do we strictly use 55°F and 95°F, or apply the 20°F difference rule based on room setpoints?
  • Any official interpretation or experience from reviewers would be helpful.

Thanks in advance!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 01/30/2026 - 16:45

The Baseline supply air temperature should always be 20°F difference from the design room temperature, with the only exceptions being labs (17°F), heated-only systems 9 and 10 (105°F fixed temperature), and the supply air temperature reset requirements of Section G3.1.3.12 for VAV systems. 

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.