Hi Marcus,
We've a LEED CS certified building in which the Tenant will occupy almost 100% of the total area, so we will fall in CASE 2.
We obtained the CS certification EAc5.2 credit and we've submeters which monitor Lighting, HVAC and receptacle equipment (only for common spaces) consumption.
Our intent is to pursue for CI EAc3 with option B, but it is unclear to us if we need to install dedicated submeters or not, and, most of all, what we need to include in the M&V plan in order to obtain the credit.
Thank you in advance for your help.
Regards
Redy
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
May 7, 2015 - 11:33 am
Option B is almost always impossible to apply to a whole building. If you have any interactive energy efficiency strategies like building envelope or lighting improvements you can't use Option B.
Option C is typically by far the easiest one to apply assuming you have access to a reasonable data set of comparable building energy use.
Whether you need to install submeters in the remaining spaces depends on the option you choose and the cost impacts. In a larger building Options B and D would likely requires some whole building submetering of building system like you have done in the common spaces. You always have the option of gathering the data through other means (by hand and with short term trending devices) but those come with a very high labor cost in many cases.
The IPMVP tells you the required content of the M&V Plan for each Option.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5931 thumbs up
May 19, 2015 - 4:11 pm
Please not that Option C referenced in my comment above is no longer available for this credit.