CI-2009 EAc1.3, Motor Variable Speed Control

I am working on a tenant build out where all the equipment is existing, as part of the recent core and shell build. The credit requirement is to show less than 30% of design wattage occurs at 50% of design flow. To do this, I assume I need the fan and pump curves for every unit, where I would convert the hp at 50% flow to kW. If I take this approach, then do I need to upload the fan curves for each piece of HVAC equipment in the project (AHU's, boilers, pumps, OA fans)?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/08/2019 - 16:58

Yes you need the curves to fill out the information in the credit form but you do not appear to have to upload the curves themselves.