FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Choosing an HVAC system baseline for a Manufacturing Facility

We are working on a manufacturing facility for which we are trying to choose the accurate HVAC baseline system for energy modelling. According to ASHRAE 90.1 2007 Table G.3.1.1A, looking at our conditioned areas, number of floors, usage and heating source as specified in Table G 3.1.1A, we need to choose "System 6 – Packaged VAV with PFP Boxes" as the predominant HVAC system. We have high thermal loads in certain conditioned zones of the Process spaces. These Spaces make up 44% of the total conditional space area of the facility. Therefore, we wish to avail of G 3.1.1 Exception (a) to “Use an additional system type for the non-predominant conditions” for these spaces as they are more than 1900 Sq. M as required by Exception (a). Further we would like to avail of G3.1.1 Exception (b) to choose "System 4 –PSZ –HP" as our baseline for these Process Spaces under discussion here. It is our understanding that we are allowed to do that as per this interpretation from ASHRAE dated “Interpretation 90.1-2007-05 - January 23, 2010” on their website: https://www.ashrae.org/standards-research--technology/standards-interpretations/interpretation-for-standard-90-1-2007 This interpretation says we can apply System 4 as the baseline for these process spaces as long they form the "lesser portion" of the building but doesnt specify a limitation on how less they have to be. Since the rest of the conditioned spaces of the building make up for 56% of the total conditioned area, Are we good to go with this methodology for choosing System 4 for the Process spaces? Thanks. Ashwin Kumar

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 02/17/2014 - 16:56

Sounds like you are entering Table G3.1.1A with the total area. That is not the correct approach. If you are going to apply any of the exceptions to G3.1.1 you first break up the project into the distinct areas. Whichever area is greatest use that to enter Table G3.1.1A as this is the predominant condition. You then apply the exceptions to each of the other areas in turn using Table G3.1.1A and applying applicable exceptions. In your case it sounds like you have two areas and the predominant one is 56% of the total. Use this area to enter Table G3.1.1A. You would then apply any applicable exceptions to the remaining 44%. G3.1.1 Exception a only applies to the two situations listed (residential/nonresidential and heating fuel source). So it does not sound like you can use that one.

Thu, 05/15/2014 - 09:57

Marcus, Thanks for the clarification on choosing the exceptions and area break up, . We have relooked at the areas (after Design reached completion) like you described and have found that 80% of our factory floor can be mapped to System 6 as described above being the predominant area, the remaining 20% of areas have high thermal loads due to 'Process Equipment'. But when you point out that - G3.1.1 Exception only applies to two conditions (Resiidential/Non Residential and heating source). Does that mean we cant model these Process areas with a different HVAC baseline by using the Exception? Please guide us on how to model the baseline for the process areas with high thermal loads. Thank You. Ashwin

Thu, 05/15/2014 - 13:25

Review exceptions b or c to see if they apply since exception a does not appear to apply.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.