I have a query on ASHRAE 90.1 2010. There are 2 paths to specify the chiller COP. How do we enter the part load values in the simulation software? ASHRAE only mentions the IPLV.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5914 thumbs up
May 22, 2015 - 9:37 am
Part load values are entered in the chiller curve. Each simulation software would be somewhat different in where to enter this information.
Jean Marais
b.i.g. Bechtold DesignBuilder Expert832 thumbs up
May 22, 2015 - 10:03 am
I humbly disagree:
IPLV (and SEER,etc.) is a rating value that is the result of physical tests on a physical machine which happens to behave in a way that can be described using (part-load) performance curves or performance matrixies (note the plural). If you run your simulated chiller, the software should be able to reproduce the IPLV rating value based on the curves and simulated laboritory test boundry conditions. The tests are slightly different depending exactly on what kind of machine it is. Not all softwares are equally good at doing this and some require improvement to correct some aspects not considered.
The fact remains that two completely different performance sets (curves) can produce the same IPLV rating value. You can make nonsense curves to do this which will make your chiller behave completely unrealistically or use a very intellegent procedure to produce a "baseline" curve derived to be as close to the proposed machine's real curve as possible whilst still producing the desired IPLV value. No software does this.
In my experience, this is one of the weekest parts of the standard at the moment, but we are working to correct it. My advise is to use a real machine's curves of a machine that as closely matches the baseline capacity and type as possible and live with the fact that it's performance and IPLV may be slightly better than the required baseline IPLV rating value.
Note that these curves are usually normalized around a rating point and use the COP and Full Load Capacity at that point.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5914 thumbs up
May 22, 2015 - 10:40 am
I don't think we disagree. I was vague and unclear and you were more thorough and precise. It is all about the curves.
Haojie Wang
Energy ModelerKJWW Engineering
4 thumbs up
May 22, 2015 - 11:41 am
Trace 700 has built-in ASHRAE 90.1 2007 and 2010 library. They have created the curves for all the equipment in ASHRAE 90.1
Rathnashree Bharadwaj
4 thumbs up
May 25, 2015 - 2:24 am
Thank you