FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Chilled beams with default occupancy

Hello,

We have an office building designed with DOAS CAV (20degC ) and active chilled beams with induction factor of 4 (at 18.5degC). The fresh air for higenic reasons is 40m3/h*person, however it has been increased to 50m3/h*person in order to make the active chilled beams work to cover peak space cooling load.

The design occupancy is 6m2/person. The designed system with design occupancy provides low summer unmet hours due to high supplied air volume working together with the active chilled beams.

However, for CS LEED compliance, we have been asked to change the occupancy to default values (23m2/person). if we use 50m3/h*person with lower occupancy, the active chilled beams are not able to cover the peak summer gains. Therefore we will need to supply around 150m3/h*person to keep the active chilled beams working in order to cover the cooling loads with high solar gains. This means that even with lower occupancy (23m2/p), the total supplied fresh air is quite similar to the case with 6m2/p. 

At the same time, the baseline case is modelled with a VAV system 7. I understand that the baseline case should be modelled with the outdoor fresh air per person as per local regulation and does not have to the same as the proposed case (in our case 40m3/h*person).

In this case, the building performs much worse when using 23m2/person than when using 6m2/person because of the required air with lower to make chilled beams work.

I would like to ask what is the best approach in this case.

- Should we model with 6m2/p as per desing specifications, or with 23m2/p as per CS default occupancy to match other LEED credits?

- if we use 23m2/p, how can we overcome the issue with active chilled beams and worse performance compared to the baseline case than when using 6m2/p?

Thank you in advance.

Regards,

Manuel

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/21/2020 - 15:33

Are you specifically being asked to apply the default occupancy within the energy model? If you can provide supporting justification for the design occupancy as a realistic value for the anticipated operation of the building, and this value was used to design the DOAS, then it should be used in the model. The Baseline outdoor airflow should be modeled as the local requirement, calculated using th same occupancy as the Proposed case.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.