Schools-2009 IEQp3:Minimum acoustical performance

Ceiling Clouds

We have a music room with some hanging ceiling clouds that contain acoustical ceiling tiles with a high NRC (.90). Can we count the cloud areas twice? They hare hanging more than 3' from deck above and both faces of tiles are exposed. I am assuming NRC coefficients are equal on both faces. Has anybody tried this before?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 11/08/2012 - 17:24

Hi Eri Unfortunately, it's not as easy as being able to count the cloud areas twice. There is an increased performance benefit, but you will need to calculate the reverberation time of the space to meet the LEED requirement that way, instead of going the square footage of treatment route. What will happen with the clouds is that the absorption coefficients behind the NRC value will increase. The only way to appropriately represent this is by calculating reverb time using the improved absorption coefficients.

Thu, 11/08/2012 - 18:43

So, would it be enough to use the ANSI calculation path, where I measure the space volume and include the absorption coefficient of different materials at 500, 1000 & 2000 Hz? ...Can in this case count the ceiling cloud area twice? that is the only way I can achieve .6 or less. I don't know if I am missing something or is there another type reverberation time calculation that I should do.

Thu, 11/08/2012 - 19:14

You would use the ANSI calculation path, but you would use improved/revised absorption coefficients for the panels to take into account the open sides of the clouds. These would need to come from the manufacturer or estimated based on a similar product. Armstrong, for example, sells a cloud product called Soundscapes that uses their NRC 0.9 ceiling tile and publishes acoustic data. Doubling the panel area would not be the correct way to do the calculation.

Thu, 11/08/2012 - 19:29

Daniel, It seems it is getting more complicated than I originally thought. We may need to hire an acoustical consultant to perform this calculation, as I am a simple architect. Thanks for your help.