Forum discussion

CI-2009 EAc1.3:Optimize energy performance - HVAC

CAV - How to meet section 3.1 requirement

Hi, For one of my LEED CI project, air distribution is a CAV system. There is a VFD for AHU though. To document EA c 1.3, i need to meet CPG requirement. But Sec 3.1 of core performance guide specifically says that VFD should be for VAV systems. In this regard can i still meet the compliance by showing VFD for CAV system? Please clarify Thanks Sriman

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 03/21/2013 - 17:39

I'm guessing you meant section 3.10 and not 3.1? I'd say that they are not applicable since the VFD will never ramp down the AHU to 50% of it rated flow. The VFD in this case reduces the energy consumption and maintins flow with small flutuations in fan speed, but should not go as far down as 1/2 the flow rate.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.