Forum discussion

CS-2009 EAc1:Optimize Energy Performance

"Categorized as an Office Space"

We are proposing a new mixed use multi-story to be submitted under NC, v2009. The first floor will be cold dark shell space for future retail/restaurant tenants. "Temporary" electric unit heaters will be hard-wired into the shell spaces. Because these are tenant spaces, we don't think we can get away with calling this a Heat Only/System 10 space under requirements of Appendix dn G3.1.1 exception e. Because we don't know what the future occupancy will be, we're looking at Table G3.1 sec 1.c and seeing that "the space shall be categorized as an office space". 1) To categorize the shell as an office space, are we supposed to assign arbitrary/typical values for people and equipment in those spaces? Lighting would be prescriptive, per space-by-space method. 2) For purposes of Table G3.1 sec 10.c, would the Temporary unit heaters be considered a heating system? Or, would these be ignored and the "future" condition (electric / System 6) be used instead? Thanks for any perspective you can offer.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 05/01/2017 - 13:49

The LEED v2009 BD+C Reference Guide CS Appendix 1 and 2 provide you with the guidance you need for these spaces. You must model all spaces as if they are fully occupied. 1. There are default values to use in the Appendices above. The space is then modeled identically to the baseline. 2. Ignored.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.