Forum discussion

NC-v4.1 EAc4:Grid Harmonization

Case 3 - On-site electricity storage

How is the use of batteries evaluated under case 3 "On-site thermal and/or electricity storage: demonstrate that strategy reduces on-peak load by at least 10% as compared to peak electrical demand". 

The battery is charged by solar panels. However, the credit documentation clearly states that on-site electricity generation cannot be included. We intend to use the battery as a backup solution and expect to reduce peak load by up to 10%. Will this strategy qualify for 1 point? Has anyone had experience with similar solutions?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.