FAQs about EAp2 :

We have installed submeters on our building but the utility bill includes energy use from several other buildings located on the same campus. How do we reconcile this during the LEED review process?

When is it possible to exclude up to 10% of the building from EAp2?

What do I do if the number of building occupants, operating hours, or vacant space changes during the performance period?

If you pursue the streamlined path for an Energy Star label, should the performance period for EAc6 match the 12-month time frame of the label?

How do I account for computers with multiple monitors on Portfolio Manager?

How should I treat vacant space on Portfolio Manager?

Our building includes a large laboratory space. Can our project benchmark under the Labs21 program?

We have an international project and the space type is eligible for an Energy Star rating. Can we pursue Case 1 to demonstrate compliance given the recently released alternative compliance paths for international projects?

We have a number of buildings on a single campus that we would like to certify at the same time. Is it possible to benchmark the buildings at the campus level?

I have a mixed-use building and am wondering if it is possible to pursue the prerequisite through Case 1. How do we proceed?

We have a building that consists of two attached structures and it’s unclear if we have to consider it a single building or if it should be certified as two separate buildings and benchmarked accordingly. How should we proceed?

How long is an Energy Star label valid to use with a streamlined approach for Case 1?

Our building includes heavy process loads that significantly increase the overall energy use in the building. If we submeter these loads, can we exclude this energy use for benchmarking purposes?

View answers »

Forum discussion

EBOM-2009 EAp2:Minimum energy efficiency performance

CASE 2 and EAP2 Cumpliance

Hi, We are working on a multi tenant enclosed mall with aproximmatly 120.000, to be certified LEED 2009 EBOM. In Portfolio Manager, "enclosed mall" is not eligible to receive EnergyStar score. According to the requirements of EAP2, not eligible buildings should consider CASE 2. Reading the reference guide it seems that for CASE 2, I can choose without any restriction one of the three options (2a,2b and 2c) in order to cumply with this pre requisite (Project Outside US). Is this correct? Thank you in advance!

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 10/29/2014 - 15:47

Joao, Yes, if you're using Case 2, Option 2, you can use Option 2a, 2b, or 2c at your discretion. But keep in mind that in general, you can also use Case 2, Option 1. I cannot recall if it offers you "mall" as a space type, but if if does, you can use Option 1.