Can't open LEEDonline forms for each building in campus project?

Hi, We are certifying a campus project with the new leed online: https://www.usgbc.org/leedonline.new For some credits we are asked to fill in forms for each building, such as IEQp1, etc. The credit form says: Project building with which this form is being completed: However, I can only open one form for that credit, does anybody know how to open new forms for more buildings? Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 02/28/2014 - 12:05

Please use the following procedure for prerequisites & credits that must be documented on an individual building (or space) basis and, thus, require multiple forms: a) Complete the LEED Online form as normal for the first building/space that is part of the project. b) Save copies of this form to your personal computer for all subsequent buildings/spaces that are included in the project. If the “Save a Copy” button is not already visible in the Adobe toolbar above the form, it can be added by right clicking on the toolbar, selecting “More Tools,” scrolling to “File Toolbar” and selecting “Save a Copy.” c) Complete all copied forms offline. d) Upload copied forms and accompanying documentation to the “Special Circumstances” section of your online form. Be sure to name files in such a way that it is clear to which project building/space each document or form pertains. There is also usually a field at the top of these non-Group credit forms where the name of the particular building (or space) for which the form is being completed should be entered. These should match the individual building (or space) names/IDs entered in PIf2 & PIf3. NOTE: Adobe Reader may not allow you to save changes to the offline forms you have downloaded. Therefore, you may either use Adobe Acrobat, which will allow you to save your edits, or you may complete the form(s) on your computer and print a copy to PDF (or print a hardcopy & scan as PDF), which you can then upload to the Special Circumstances section of the main (live) form in LEED Online.

Mon, 03/03/2014 - 14:32

Thanks very much Eric, this is of great help!

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.