Campus approach: can we install water meter for the entire landscape, sanitaryware as a whole

My project is a campus project, consisting of 4 individual buildings. To fulfill this credit, can I install 1 meter to monitor sanitaryware for 4 buildings together as a whole? or I have to split into 4 separate meters for each building.

Regarding water for landscaping, can I have just 1 spot of water supply with 1 meter for irrigation for the whole site, or do I have to split into 4 water supply locations with 4 separate meters for each building? Thanks for your advice.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 08/25/2022 - 13:21

The Water Metering credit is ineligible for campus approach. Each LEED project would pursue the credit individually. So you would need to have a meter representing sanitaryware for each building. Same with landscaping - the water supply for each building would be needed metered. If this was a group project you could get away with metering the irrigation system once, but you cant for campuses. 