Forum discussion

EBOM-2009 EAc3.2:Performance measurement - system-level metering

Calibration

Hallo, According to the BMS and HVAC subcontractor, the sensors do not need to be calibrated, particularly CO sensors and chilled water temperature sensors. For AHU's air supply temperature sensors, they recommend replacing them if they are "out of range" Is this a common practice? What specific sensors need to be calibrated? Thank you.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/29/2017 - 15:45

For this credit, the energy meters need to be calibrated rather than BMS and systems sensors. Proper function of sensors and actuators is addressed under EAc3.1 and can be demonstrated via a robust BAS maintenance plan.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.