When utilizing CA Tilte 24 as the referenced standard, will this meet the requirements of this prerequisite for mandatory and prescriptive requirements and lighting power density requirements? Would attaching the report generated by Title 24 software (EnergyPro) that utilizes the performance approach to the buildings energy use satisfy the documentation and would this be attached under the "alternative compliance path" section of LEED Online?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for $12.95 »
Erik Dyrr
Director, Sustainable Buildings and OperationsKEMA
80 thumbs up
March 29, 2010 - 12:00 pm
Doug,
Technically, this approach would not work, as the PERF-1 Report to which you refer to is in reference to the fact that an energy model is a "Performance" approach to achieving Title 24. In a "Performance" Approach, you DO have to comply with the mandatory requirements of the standard, but you do NOT need to comply with the prescriptive ones.
That said, EAc1 and EAp2 in NC (aka BD&C) have long accepted that a building that complies with a performance approach meets the requirements of the prescriptive approach. If you feel that this approach is your best option, submit it and if the reviewer says that it's inappropriate, you use the prescriptive approach as your Review Comment Response.