FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Building system types vs square footage and non-predominant uses

I'm working on a project that totals approximately 178,000 sf, of which approximately 140,000 sf is office space (3 stories tall), with the other 38,000 sf being conditioned manufacturing space. In determining what the baseline systems are, I'm not sure which square footages I should use. Under the exceptions of G3.1.1, the manufacturing area should have a baseline HVAC system of Type 3 or 4. If the gross square footage of the entire building is used (which is over the 150,000 sf threshold), that would make the baseline HVAC system for the predominant office occupancy be Type 7 or 8. But, since the manufacturing area is broken off onto its own HVAC system type, shouldn't the predominant office occupancy be judged on the 140,000 sf that it takes up, rather than the total building gross square footage, and thus have a baseline HVAC system of Type 5 or 6?

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 07/11/2012 - 22:46

I think this is debatable. It is our opinion that the total square footage should determine the HVAC system type for the baseline and then the exception is applied to the applicable space. Applying the exception does not lower the total square footage. So I would say a 7 or 8.

Fri, 07/13/2012 - 15:53

I checked into this further and apparently the debate is over. While I still believe that our opinion above makes the most sense, apparently GBCI has decided otherwise. So the square footage to which an exception is applied is subtracted from the total and then the remaining square footage is used when entering Table G3.1.1A.

Mon, 11/19/2018 - 15:33

Marcus...do you happen to have the website location of the full interpretation text from GBCI that you referenced as I can’t seem to find it. I totally understand if you can’t recall as it was 6 years ago! Additionally, thoughts on if the # of floors would also decrease? Example: I have a 154,000 7-story building but 2 full floors fall under the exception B, therefore can I “enter” table G3.1.1A with a 110,000 5-floor remainder to determine baseline system in lieu of the 7 floors (this would result in a system type 5 versus 7). Let me know your thoughts and if you can find the GBCI text. Thanks.

Tue, 11/20/2018 - 17:50

Consistency-wise I think your approach makes sense Josh, that the floors should also be exempted.  Can you also check the 90.1 User's Manual? I don't recall right off-hand, but perhaps an example has been added since that time to clarify the intent of the system selection algorithm. The question obviously has come up a few times. I can see Marcus' approach making sense where the exempted areas are relatively small. If we envision a building that is on the edge of the total area threshold and has a 60/40 split it would be less intuitive that the predominant 60% should have the total area/floors and not the net of area/floors after the exemption.  

Tue, 11/20/2018 - 18:35

I do not think this was ever codified in a LEED interpretation. This was decided by GBCI internally and I am not aware of it being made public except for above.  I agree with David, logically the number of floors could decrease as you apply exceptions as well under the current rules. Interestingly enough I think you could now probably make a case for not reducing the building area/floors since the 90.1-2013 User's Manual clearly states that you should use the entire gross building area to determine the baseline system type (page G-33 to 34). As I had indicated years ago it never made sense to me to reduce the area to determine the baseline system and the 90.1 committee seems to agree. Projects can and do look to subsequent versions of 90.1 to provide answers relative to the ASHRAE 90.1 committee's intent when the currently used version in LEED is unclear. When this was originally posted 90.1-2013 had not been released yet and I had not really gone back to take a look at this particular issue. So thanks for bringing it up again Josh. I guess the debate can continue!

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.