I'm currently involved in a project which is served by buses only (15+ different routes).
Do you know if the above is suitable for the Access to Quality Transit Credit?
Can the multiple bus routes qualify as multiple transit?
Thanks you in advance
Summer Minchew
Managing PartnerEcoimpact Consulting
LEEDuser Expert
164 thumbs up
December 13, 2019 - 8:10 am
Yes, multiple bus routes within 1/4 mile walking distance from the functional entrance of your project is acceptable. You do not have to have a bus and a streetcar, for example, in order to comply with the credit. You will use Table 1. Minimum daily transit service for projects with multiple transit types (bus, streetcar, rail, or ferry) to determine points based on the number of qualifying routes.
alfonso senatore
Managing Directorongreening consultancy
December 14, 2019 - 7:16 am
Many thanks Summer for your reply.