We are working in a Garment Factory project in Sri Lanka where the facility is to be LEED certified. Whole building will be put up as a non air conditioned facility. mechanical ventilation systems would be installed to provide fresh air to the building. since the facility is located in an area with a tropical climate occupants are assured to have required thermal comfort.
But the problem we are having is since ASHRAE 90.1 is developed for Air conditioned facilities is it possible for us to claim energy savings for this particula facility through an energy simulation based on ASHRAE 90.1 standards. We will not claim any credits for air conditioning and only hope to claim credits for savings on artificial lighting. will this procedure be accepted?
if the above is not possible should we go for a manual calculation to prove energy savings? but the LEED guideline says manual calculations are accepted only when the simulation can not be used to reflect the actual scenario. how would this clause affect here? please advice on the best way forward. thanks in advance.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
December 9, 2011 - 11:04 am
You are required to include air conditioning in both models by 90.1. Simply model the air conditioning but set the temperatures the same and high enough so that it does not come on.
Udana Ratnayake
121 thumbs up
December 20, 2011 - 1:48 am
Thanks Marcus. so does that mean even we don't have air conditioning installed for real in our project it is possible to simulate the building as per ASHRAE 90.1?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5907 thumbs up
December 20, 2011 - 9:22 am
Yes it is possible for LEED.