Forum discussion

CI-2009 IEQc3.2:Construction IAQ management plan - before occupancy

Building Flush Out - Chilled Beams / Radiant Cooling

We have couple of projects where the HVAC system is being served by Chilled Beams and Radiant Cooling. I would like to know is there any specific method for carrying out building flush out with 100% DOS system.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 07/06/2012 - 15:34

There is no specific different method for going about a building flush out with 100% DOS. The only caveat is that typically a DOS system is between 20-50% of the size of a typically VAV system with min OA that would serve the same size project. As a result you may need to schedule more time in the construction schedule to finish the flush out over a typically VAV system capable of economizer. If the construction schedule is tight you can bring in temporary supplemental fans to speed up the flush out.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.