Our project has included Building Envelope Commissioning as part of the scope of Enhanced Commissioning plan. My queries: 1) This is to seek confirmation if the test methodologies listed in ASTM E2813-12 suffice to meet LEED requirement under Building Envelope Cx, or if there are other standards that need to be referenced? If so, which other standards? 2) In the table, there are only 4 mandatory lab tests. The rest are optional. Will performing the 4 mandatory lab tests be sufficient or will LEED look for a few optional lab tests? If so, which ones or how many? Hoping for some advice. Thank you Pabs
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Add new comment
To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.