FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Building Area Method - Interior LPD

Dear Concern:-

 

we have recently submitted the LEED V3 NC project  for review , our project is office building so entire project has been reflected with a lighting power density (LPD) of 1.0 W per square foot in the Baseline model but the review comment was different

Review Comment:-

 

"using the Building Area Method, a separate LPD value for each major building type must be reflected in the Baseline model using Table 9.5.1. In this case, an LPD value of 1.0, 0.8, 1.3, and 0.3W per square foot must be reflected for the office, warehouse, manufacturing facility, and parking garage portions of the building, respectively. For future projects, if using the Building Area Method, ensure that the appropriate LPD value from Table 9.5.1 is reflected for each major building type in the actual design"

 

So my Doubts are 

 

1.is it needed to model the each space with different building type as per ASHRAE 9.5.1 ???

2.is it correct to model the same interior LPD for Building ????

 

now we have lot of confusion after getting this review comment kindly help us how to respond this review

 

additional Explanation needed for below Queries

 

i.Building are method for Interior LPD is vary for Each space or Each Building ?????? 

ii. we have two building in site and each building have 56 spaces each but both working function is different so we have modelled with different LPD for both building   A. is it correct ????  B.is it required to model those 56 spaces with different LPD as per ASHRAE 9.5.1

 

*we have followed Building area method for Basecase Interior LPD

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 02/02/2018 - 23:05

It sounds like you need to correct the models. 1. Yes, if those distinct space types include a significant area of the building. 2. Under the building area method you are supposed to model each space in the building identically within that building type and you are supposed to model all building types that apply. Note that Section 9.5.1 indicates types in c and d, not just one building type. This will often provide some gray area so you need to apply some common sense. In your case the project sounds like it has those 4 distinct building types. Many of those building types within your building could be operating on different schedules so that would be an indicator that a different type may be necessary. If the building types within your project has significantly different LPD requirements that would also be an indicator. It is certainly not fair to model an office building with a parking garage as all office in the baseline and the proposed is a combination, for example.  We almost always use the space-by-space method as it is far more accurate and usually generates more savings.