NC-2009 SSc7.1:Heat island effect - nonroof

Building and trees shading

Dear all, I'd like to discuss 2 issues: 1- Our project has most of the parking spots outside, at ground level. At the same level, there is an area for parking, under columns ("pilotis"), of total 5,102sf. Is it possible to consider this area under the bulding, but adjacent to the outside ground floor, as hardscape? This way we could consider this part of the hardscape shaded. 2- For the calculation of the shadow of the trees, we're using the 10, 12 and 15h shades. But as the trees are close to the boundary of the site, at 10a.m. the shade goes ouside the site. Nevertheless, should we still go for the arithmetic mean of this 3 times of the day? Thanks a lot!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/10/2015 - 15:49

Covered parking automatically qualifies if the shading device (your building) has an SRI of 29. For the tree shading, what you care about is the shadows that fall on hardscape within your LEED boundary. Shadows that fall outside the LEED boundary, or on the lawn, don't make any difference to you. Calculate the total hardscape (except the parking under your building, that automatically qualifies) and the shaded hardscape, then calculate the ratio of shaded hardscape to total hardscape.