Hi, for the HVAC Equipment points (5), our project meets the requirements of sections 1.4 and 2.9 of the core performance guide but not 3.10 since the system is constant volume (as most VRF and inverter split unit types are). Does this mean we cannot score any points at all?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
January 7, 2015 - 2:27 pm
Correct, you must meet all three criteria to earn any points.
Chilufya Lombe
Sustainability ConsultantSolid Green Consulting
30 thumbs up
January 12, 2015 - 3:10 am
Thanks Marcus. Our only hope for the full 10 points is via the modelling route then, although 30% HVAC saving is quite challenging.